Hello, i am planning to install an Endress and Hauser Gas Flow Switch to an IS DI Namur Charm, however the instrument requires constant power between 18-30 VDC (Not loop powered). On the S Series installation manual I can see that the switched output signal of my instrument connects to terminals 3 and 4 of my IS Charm terminal block, but I want to be sure that I can supply field power via terminals 1 and 2. Also my instrument requires approximately 3.0 watts of power, and I want to be sure the IS charm terminal block can supply this. Am I also correct in assuming that no barrier is required to supply this power to the hazardous area ? I am new to DeltaV hardware, so I apologise if this is an obvious question. Many thanks. Aidan