We have a new Emerson PK controller and need to communicate to a PowerFlex 70 over Ethernet/IP. Now we’ve done this with a “regular” DeltaV controller using a VIM module. But it seems the same settings are not working here. Need to check some more. I know the PK is somewhat new. But has anyone here got this combination to work? Must be a setting somewhere, but there are many of them. Any help will be much appreciated.
In reply to Nathan Hunt:
In reply to jakerekes:
Jake, Did you use explicit class 3 messaging? I'm currently using class 3 explicit: Class ID 15 (parameters) Instance ID 31 (motor nameplate volts) Data Description: Input, byte offset: 0, Data type: 16uint, Byte order: Big End, Word order: normal, All bits usedAttribute ID: 1 I'm expecting to see 230 as that's what the power flex 525 is setup for. I'm getting bad integrity and no device comms from diagnostics. Any advice? Thanks
I ended up using the following configuration: Class ID 15 (parameters) Instance ID 31 (motor nameplate volts) RPI 500 Connection Priority: Low (found this in a NK document) Data Description: Input, byte offset: 0, Data type: 16uint, Byte order: Little Endian, Word order: normal, All bits used Attribute ID: 1