Emerson Exchange 365
Search
Sign-In / Register
Site
Search
Sign-In/Register
Services
Products
Control & Safety Systems
Asset Management
Measurement Instrumentation
Valves, Actuators & Regulators
Fluid Control & Pneumatics
Electrical Components & Lighting
Welding, Assembly & Cleaning
IIoT & Digital Transformation
Industries
Chemical
Food and Beverage
Industrial Energy
Life Sciences
Oil & Gas
Power
Refining
Other Industries
Women in STEM
Events
Düsseldorf 2024
Immerse - Anaheim 2023
Grapevine 2022
Nashville 2019
San Antonio 2018
The Hague 2018
World
China
South Korea
Russia
Products
More
Control & Safety Systems
DeltaV Forum
DV_PRO+ STATION
Forums
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent Control & Safety Systems Discussions
Eric Franco
4 Aug 2020 4:55 PM
Alarm Summary Export
7 Replies
AlejandroQuiroga
4 Aug 2020 4:18 PM
Use STATUS parameter of I/O cards in Calc Block
4 Replies
krishna sen
2 Aug 2020 6:23 PM
Syntax_error
8 Replies
krishna sen
2 Aug 2020 1:34 PM
Alias_Function
0 Replies
fkitzmann
21 Jul 2020 5:54 PM
HART CHARMS problem causing MODBAD on AI and AO blocks
5 Replies
<
>
Similar Posts
Engineering Station (P station)
Moving the Full Span of Control License from one Professional Station to another Professional Station
Operator station error
work station configuration problem
RPC Failure in P Station
Share
DV_PRO+ STATION
Dear Experts
We are using the DV 10.3 system. Suddenly our pro+ station windows has crashed and we have to reinstall windows and DV software.We have recovered the database with the following sequence:
1. Open "Database Administration" and select "Create New Database".
2. At the first window give the database a name and select Next
3. In the next window create a new database from an existing export file , find the recent created (.FHX) file and create the database.
4. Once i have successfully done so, go to "Set Active Database" and "Change" with the just created database.
But my question is if i change 'active database' then it will disrupt synchronisation between online controllers and DB and for restoring this synchronisation i have to full download all controllers in deltaV system.Now our plant is running condition and full download of controllers is not possible at any cost.So please guide me how can i take professional plus station in deltaV control system without taking shutdown of our plant.
2 Replies
Lun.Raznik
9 Aug 2020 6:56 AM
As other have said in the forum, cases like this, call GSC.
Would you happen to have a recent copy of <DvData>\PowerUp folder from DV_PRO+? Also, how recent is your FHX backup? If you have recent backups for both, your restore will work fine, thus say,
- Copy PowerUp from backup to <DvData>\PowerUp
- If you have database backup, then do a database Restore using DeltaV Database Administration, this is the fastest to recover. Otherwise, import FHX.
By the way, on most cases, DV_PRO+ is not needed during normal operation except for OPC browsing. So, as an alternative, run the plant until it is safe to do download.
There was also an extensive discussion recently on the same topic, see below:
emersonexchange365.com/.../19737
LaurentB
9 Aug 2020 7:19 AM
In reply to
Lun.Raznik
:
Hi.
I strongly recommend you to call GSC to help you.
Lun Raznik gave you a nice shortcut to recovery your online DB. That requires. Up to date FHX and Powerup directory. ( try to get this folder back from crashed p+)
As also said P+ is not required for normal operation, but whitout powerup restore, you will not be able to perform any partial download.
For the future I strongly recommend you to contact you Emerson representative to order DeltaV backup and recovery solution , which allow daily automatic backup ,but also a fast and easy way to restore.