CHARMS CSLS IO cards periodic failure at every 24hrs intervals which causes an OSD trip at every 11:14 AM on daily basis.
At this particular time 11:14 am all the CHARMS CSLS IO cards red lights flashes within some seconds and then all the AI cards and some few DO cards will
normalize while about 90% DO cards will go completely powered OFF and shall require re seating the affected DO cards before they will normalize to start up.
Initially when this issue started at every exact time it will occur all the CHARMS CSLS IO cards (AI & DO) flashes red and normalizes within a few seconds and
all the CHARMS CSLS IO cards will recover but presently only the AI cards recovers and the DO cards will require a re-seat to normalize.
Both CHARMS IO (AI & DO) shares the same back plane.
Both active and redundant CHARMS CSLS has been changed,decommissioned and commissioned again and the issue persist.
Observation: When the CLS was decommissioned, power cycled, commissioned and downloaded all the AI cards will normalize but the DO cards must be re seat
before the normalize.
Please I need some help.