So we have 16 thin clients that have an Internet Explorer button on the DeltaV Operate Toolbar for anyone to access. It goes to an internal website for looking at data.
One of the thin clients stopped working, clicking it opens an Internet Explorer window for a split second then it closes.
If I login with my admin account, and go into Windows Desktop (FlexLock) I can open DeltaV Operate and use the Internet Explorer not problem. It only doesn't work when in DeltaV Desktop mode (FlexLock).
I don't really understand FlexLock or what the difference is...
What is stranger, if I login to the VM as an Administrator I am able to use the Internet Explorer in either DeltaV Desktop or WIndows Desktop mode.
It seems like a permissions glitch, but I don't know where to start because FlexLock seems to be the problem.
Any insights, thanks?
How does your button call the application? I believe the function frsruntask is the only safe way to call an external application to ensure it appears on the DeltaV Desktop. Otherwise, I suspect you are piling up internet explorers on the Windows desktop.
In reply to Youssef.El-Bahtimy:
In reply to Brodie Hinch:
Andre Dicaire
In reply to Andre Dicaire:
What's great about thin clients and terminal servers is that because the real action happens at the server, we usually have more data point samples (i.e. the other thin clients on the same terminal server), or less variables to worry about (i.e. the client build itself is irrelevant, typically).
Let's build a table to correlate:
We need to determine if another OK client is assigned to the same terminal server as the problem client.
If so, then we only need to compare the properties of how that OK client connects to the terminal server, and especially to DeltaV to isolate it.
Additionally, we can correlate to another terminal server and an OK client on that one for added data points.
I have added several properties which could impact the client once they connect. They are:
1. Client Session : Is the client programmed to automatically grab and hold on to a particular remote client session as depicted in DeltaV Explorer (Under the terminal server operation station's remote client subsystem?) . Is this session markedly different than others?
2. OS User: Is the client programmed to automatically log in to windows on the terminal server as a different OS user than the ok client on the same terminal server
3. DVUser: Is the client programmed to automatically log in to DeltaV on the terminal server as a different DeltaV user than the ok client on the same terminal server
4. License : Is the dedicated Client Session in DeltaV Explorer licensed differently than the OK client dedicated session
If you don't have another client on that same terminal server, I would ask to put one on temporarily (configured identically to a client on the good client terminal server(s)) and compare.
If you do have another client that works ok on the same terminal server, log it off and log it back on. If it starts behaving like the problem client after this, (the same goes for a client on any other terminal server) then it is a more global problem. If we start seeing this or no differences between this client and the others, then we'll have to dig deeper.