I got my version 13.3 Proplus out of the box from Emerson partner. all configuration already on this machine. Plugged it in and connected cat5 directly to CSLS. the CSLS is not shown on the local safety network ->unassigned safety nodes.
I tried 4 different cat5 cables and still nothing.
I plugged directly into my SZ controller which was connected through safety switches to the CSLS still did not see it on unassigned nodes.
I plugged directly into the CSLS and still did not see it on unassigned nodes.
Yes I checked the power on both (it is fine 24VDC). When cat5 was plugged in the communication light flickered next to the cat5 plug on both the server and the CSLS.
Thanks,
pat
Andre Dicaire
In reply to Andre Dicaire:
In reply to Petrisky:
In reply to JDWheelis:
If that doesn’t work, please refer to DeltaV Books online and search for manually resetting decommissioning a CSLS. It involves powering down, and removing the Network port from the baseplate. After power up, wait for a 2 minutes for the CSLS to boot and go through self tests. Then you reinsert the network port. You have to do exactly as per the BOL procedure, see below. The wait 2 minutes is important. I spent half a day getting to the bottom of this issue when the CSLS was previously assigned to a different database placeholder.
In reply to IntuitiveNeil: