Emerson Exchange 365
Search
Sign-In / Register
Site
Search
Sign-In/Register
Services
Products
Control & Safety Systems
Asset Management
Measurement Instrumentation
Valves, Actuators & Regulators
Fluid Control & Pneumatics
Electrical Components & Lighting
Welding, Assembly & Cleaning
IIoT & Digital Transformation
Industries
Chemical
Food and Beverage
Industrial Energy
Life Sciences
Oil & Gas
Power
Refining
Other Industries
Women in STEM
Events
Düsseldorf 2024
Immerse - Anaheim 2023
Grapevine 2022
Nashville 2019
San Antonio 2018
The Hague 2018
World
China
South Korea
Russia
More
Cancel
Products
More
Control & Safety Systems
DeltaV Forum
Dongle not getting detected in particular System
Forums
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent Control & Safety Systems Discussions
Valentin Borsu
1 May 2024 5:31 AM
DeltaV PK750 Controller - Perf_Index of 2 (Asset Monitoring
4 Replies
TreyB
22 Apr 2024 9:47 PM
DeltaV Live Gem Read only after reinstall, etc.
9 Replies
TreyB
13 Apr 2024 3:46 PM
Control Studio Phantom session issue
2 Replies
Petrisky
12 Apr 2024 6:21 PM
Every (as in 300) LS DO CHARMs FAILED
5 Replies
Verx
12 Apr 2024 5:53 PM
DeltaV PK Controller EIP To Wago 750-363
5 Replies
<
>
Similar Posts
Dongles damaged
Gold Dongle
DeltaV 14.3 dongle
DST consumed by a particular Module
Search all graphics for a particular string
Share
Not Answered
Dongle not getting detected in particular System
The dongle when i plug in to the usb ports of particular system , not getting detected by the system , but getting detected in another system with same dongle Checked in WATCHIT , the error is LIC_SYSTEM_CLOCK_SET_BACK The issue came after i have installed a Symantec Antivirus software .I tried uninstalling and checked but still not working System time and zone settings was the same as ,what it was , when DeltaV Installed Please give me a solution Thankyou
3 Replies
Neil Castro
27 Apr 2018 10:48 AM
I guess you are using an SI Dongle.
On the system that shows LIC_SYSTEM_CLOCK_SET_BACK there is a big chance that you, someone, or something (Symantec) changed the machine time to a future date/time then return it to the correct date/time.
In case this is a development or a demo system I recommend starting on a fresh OS with the correct date and time while installing the OS and DeltaV.
In case this is a live system then you may want to insert the license Dongle (non-SI Dongle) intended for the system. The licensed Dongle is not time sensitive.
Hope this helps.
Regards,
Neil Castro
Andre Dicaire
27 Apr 2018 2:30 PM
In reply to
Neil Castro
:
The Licensed system dongles are also time aware for the temporary engineering seat licenses that can now be purchased for DeltaV. Manipulation of the system time should not affect the operation of the dongle in general, but could cause any time based licenses to be unavailable. Of course, if you don't have any such licenses, than there would be no impact there.
Manipulating the system time can also disrupt the History data storage. If you set time to future date, say a week in the future, and after an hour, restored normal time, there would be a gap of data for the hour time was set forward, and when the week elapsed to the start of the "future hour", there would be records overlapping for the real data and the data from a week ago, so you'd lose two hours of data. This would also mess up the Dataset time spans if the future time stamp was further than the current data set can collect into. With PI, it would result in disabling data compression and cause every value to be stored as "back in time" data, filling archive files quickly and slowing data retrieval as the quantity of data points would be orders of magnitude larger than normal.
Point is, do not manipulate system time into the future for "test" purposes on a production system, and be prepared to reinstall OS to restore normal operation.
Andre Dicaire
Neil Castro
27 Apr 2018 11:51 PM
In reply to
Andre Dicaire
:
Thanks Andre for the new information. :-)
This shows that I have been away from new DeltaV features. I need to either read documentations from Emerson that is new to me or go back to technology work.
Regards,
Neil Castro