Hi Experts,
For MODBUS communication, general MB slave can respond one master only. When there are more than one master acquiring data, how does DV deal with this situation?
For example, there is one APC PLC and two DV controllers. When both DV controllers are acquiring the pressure reading in APC unit which is tied into APC PLC, how to configure this kind of requirement? One way I can do, however, appoint DV controller A as the master to pull the reading PT1 from APC PLC via MODBUS and controller B refers to PT1. But the question is, what about controller A is down, controller B will lose PT1?
In a client-server modeled DCS system (can I say DV system is a peer-to-peer model?), there is a type of points called "server point" which is built and controlled by DCS server, all third party data are in a data pool, all DCS controllers could visit the pool for the same data acquisition at the same time.
Thanks.