The power supplies in a redundant controller deployment - are they totally independent of one another or do they load share / back up each other? So when I pull a power supply, it should only affect the controller next to it . . . in my case it would be the "Standby" controller's power supply. It only affects the "standby" correct?
My concern is around if they did have some redundancy, one might have a "weak" one on the primary which would potentially fail when the "backup" was pulled . . .
Andre Dicaire
In reply to Andre Dicaire:
In reply to John Rezabek:
Hmmm. Should work. But if you are concerned. Force active controller to right. Then remove stand by controller and install a new supply in pls e of controller. That puts three supplies in play.
Then replace the left carrier old supply. And then restore redendunant standby controller.
Now you have new supply for when you replace the right hand carrier's supply.
Note that this only slightly extends your simplex time your are in simplex operation.