Hello experts,
I was wondering if it would be possible to preserve the output from PID during a download? I've tried to find the specific donwload parameter to use it as a condition, but I couldn't.
Thanks,
Sam.
Karma doesn't have any menu, you get serve what you deserve.
In reply to Digital Technician:
Hi Bruno,
User defined Parameters are those which are created by the user(for ex:- Ouput Parameters) and critical block parameters are those defined within the function blocks(for ex:- PID1/OUT)
Below extract from DeltaV BOL:-
"Parameter download behavior
Select the download behavior. The choices are:
Preserve critical block values - The controller copies critical function block values from the executing module to the new module during a download. This selection typically minimizes disruption to the process.
Preserve user-defined and critical block values - The controller copies user-defined parameter values from the executing module to the new module during a download in addition to copying the critical function block values. Make sure to use this value if any parameters reference OPC Mirror data. If this is not selected the parameter values will change to their configured default after download rather than retaining the value from OPC mirror.
Use configured values - The controller does not copy any parameter values from the executing module but uses the values from the configuration database. "