Hi,
I am trying to configure the advanced alarming module ALM_FLOOD_SUP for alarm masking following a compressor trip and have a few questions -
1. Once the unmasking logic is triggered following AUTO_RESET and the chosen TIMEOUT_OPT is None Suppressed, is it possible to delay the actual unmasking of the alarm to the operator by a specified period of time configured on an alarm by alarm basis (e.g. using the HI_AUTO_UNMASK/TIME_DURATION parameter for a particular High alarm) ? Or does the unmasking to the operator happen instantly after AUTO_RESET?
2. Can the SUP_TIMEOUT parameter be configured to start counting down once the AUTO_RESET condition block is satisfied before unmasking all alarms? The aim is to have this timer to be longer than the individually configured unmasking timers above.
3. What is the logic that would be needed in the DYN_PRIORITY action block if the alarm priority state required is Mask?
Any other configuration tips would be appreciated, thank you.