We converted some simplex MX controllers to redundant MX controller. After that we did a little test and forced a switchover of the active controller. We did not have any issues with the associated modules inside this switching controller, but we having an interruption in historical data archiving. There was a gap of 3-4 seconds in our trends (no data / comm fail). Our Historian is an OSI Pi Enterprise server talking to an DV application station acting as OPC server. So it seems that during switchover the OPC server can't talk to the effected controller and his modules and is reporting the values as bad. Emerson is saying in their whitepaper '..the process continues as though nothing had happened..'What does this issue mean to e.g. 1. Modules with controller to controller communication during a switchover. - Other controller Module is read or writing to the switching controller.2. Control Loops / valves / drives inside this redundant and switching controller.3. Running Batches (Phases - with the default failure monitor SWITCHED_OVER parameter used.)
- Any experience/recomodations or thoughts about Phases and redundant Controllers in case of switchover?
Regards Martin
In reply to Mike Link:
In reply to MichaelP:
Screen capture of "Switchover occured" event.
Andre Dicaire
In reply to Andre Dicaire: