I would like to have an alarm priority that would allow alarms with the given priority to show up in Process History View but not on the Alarm List. I have set up an alarm priority with a value of 4 that is auto acknowledged and has no sound. I found that if I gave the priority a value of 3, it would show up as an event (not an alarm) in the Process History View and would not show up in the Alarm List. This caused a problem because it was difficult for me to sort out the level 3 alarms from all of the other events. Giving the alarm a priority of 4 or higher allows the alarm to show up as an alarm in Process History View, but it also leaves standing alarms with the given priority in the Alarm List. I can filter the Alarm List to show priorities with values of 5 through 15, and everything works as I would like it to. However, if the user navigates away from the Alarm List and back to the Alarm List, the filter is lost. I would like to change the default Alarm Summary Filter Setting to only show priority values 5 through 15. Does anyone know how to change these defaults?
Lisa Vasbinder
Andre Dicaire
In reply to Andre Dicaire:
In reply to lvasbinder: