Dear Engineers,
our plant works with PBL Library (DV 11.3), I need to modifies our _AI block, when I want to save my modification a Pop Up shows that I need to modifies my AI_SOFT block.
Unfortunately, this block is Password Protected.
Our Emerson Support is not able to help us.
What should I do now?
Your Ideas are welcome.
Kind regards
In reply to Matt Stoner:
Hello Matt
as shown on the print screen the_ AI block was not modified since revision 4.5..... in 2005.
The plant is running since 2006. I'm only on site since 2 years.... my knowledge of what happened while and immediately after commissioning is very low.
Maybe somebody could give me some "standard" passwords to try....?
Reagards
Christophe
In reply to LostEngineer0:
the solution was to contact our local Emerson support, wich could give us a non password protected module version.
I will not explain here how we proced for replacing the old module with the new, but if somebody need it I could help.
Have a nice day.