DeltaV Detail Page for Faceplate Password Protection

Hello, 

I am using DeltaV version 13.3 DeltaV Operate, we have a traditional DL_FP faceplate with DL_DT1 detail page. Operations is requesting a password protection on the bypass selector built into the detail page. 

Is this a possibility within DeltaV Operate or perhaps the script code. 

2 Replies

  • By default this Bypass parameter is password protected based on the User rights. If your operator user has elevated rights assigned to them then they are able to select Bypass. Our operator only have operate rights, so they cannot change this value. It is possible that this parameter security has been changed or deleted too.
  • In reply to KeithStThomas:

    If just the security rights Keith described isn't enough and you want operations to enter Username/Password when changing, that would Electronic Signature but keep in mind it will be always done (Enable and Disabled).

    You can find information about this in Books Online under Configuration->General Configuration->Electronic Signatures.