Hello,
We have an on/ff valve that occasionally loses the input 120V signal and Operations see "Confirmation Closed Lost" lost.
The valve is energized to close, so we have a PV - SP mismatched is what the DCS is alarming.
Technicians checked the loop electrical components.
It it possible the DI input channel is losing the valve closed input signal intermittently?
Thank you
Andre Dicaire
In reply to Andre Dicaire:
Thank you so much Andre,
I am still learning, so I may need some help on explanation.
1. We are using DI Card, 8 Ch., 120 VAC, Isolated. Only channels 1 thru 5 are in use.
2. What do you mean by "High Side sensing of the AC powered DI signal" ? We are using channel 4 (terminals +7 and -8). Is +7 the high side sensing?
3. " the DI Channel can have issues when the contact is open. " Did you mean to say issues with the limit contact is closed?
4. What means "moving to an Isolated DI wired to the low side of the contact" ? How do I accomplish this?
5. The DI card powered from the DeltaV system 12V power supply.
Thank you kindly
In reply to Bruce Brandt:
Bruce Brandt said:Emerson has released a new CHARM that has a built in resistor to address this issue. The problem is caused by induced current on the slgnal wires that is just high enough to cause the CHARM to sense it as being indicative of a closed contact depending on what is inducing the current it is entirely possible that it is intermittent, a large motor that is it used continuously for instance. A dropping resistor will fix the problem.
Thank you Bruce,
I need to mention that the distance from DI card to the field device is a bit far then when normally used. So we use a relay for induced voltage. The sensing signal is 120V.
The device contacts is normally closed and opens intermittently causing trip or Closed Confirm alarm on the DCS for the valve position. So 120V is sensed to the DI card at all times during normal operation.
Will induced voltages/currents cause the contacts to open? Maybe over current (from the induced current) on the DI card fuse cause the circuit to open?
What means " dropping resistor"
Thank you. This is good challenge for me.
In reply to DCS Newbie:
Andre Dicaire said: There is always the use of an isolation relay, which requires more electromotive force on the part of the signal to activate the relay and the coupled wire is unlikely to have enough energy to activate the relay. But you might try a test circuit to see if this solves the issue.
Thanks,
Yes, we are using an isolation relay in the circuit to confirm the 120V back to DI card.
Maybe the relay is failing at times.
Thanks
In reply to jimgraves:
Thank you for replying.
How do you resolve improper grounding for DI card?
The limit switch loop on a 120V isolated loop with a isolation relay for induce voltages.
Darrell
The condition you are discussing is possible. As per my experience with this the High Side sensing of the AC powered most of the time the DI signal the DI Channel have issues when the contact is open. The wire from the card to the contact is subject to coupling and depending on the wiring, length, and environment can result in issues on the DI. If you are using a system powered DI card on the DeltaV system, it is a high side sense circuit. Also most of the time the use of Relay is there.