hi friends,
i have a digital input that its duty is acknowledge all alarm in the system. it means you acknowledge warning, critical, ... alarm in DeltaV system.
but my question is here, how can i do it? it means how can i do it with a DI signal?
Andre Dicaire
Hi..i am a new user here. I worked different type of Alarm systems and as per my knowledge acknowledging an alarm in DeltaV requires that the alarm be visible and therefore assumed to have been seen by the operator when acknowledged. Acknowledging the alarm also results in a record in the Event Chronicle. Creating an Input DI that would acknowledge all alarms in the system without every seeing them does not make sense to me. Also silencing the HORN can be done by defining an on change event on a variable that monitors the source trigger. When the change event is detected in each console, the script can silence the horn. Alarms are not acknowledged until an operator does so at the console, but the horn can be silenced.