Hello experts,
Does anybody know how to copy the content from SIGlobals?
The goal is to have 2 new SIGlobals (SIGlobals01 and SIGlobals02) with the same content from the original and customize according to the requeriments from costumer. I've created a new SIGlobals using the attached procedure and the NA-1000-0003 to copy the color table, but I couldn't copy the treshold table and other variables.
Thanks,
Samuel.
In reply to Matt Stoner:
In reply to Samuel Bandeira:
Hi Matt,
I tried to use your code, but I it didn't work (as long I'm not a specialist, maybe I did something wrong). But anyway, I used the "Write/Load User Globals" tool from DeltaV and with that I could export all tables and variables.
I'm also using User instead a new SIGlobals, as you suggested. But I still cannot have both working at same time.
I have the original PCSD_AI FP and X_PCSD_AI FO (which is a copy from original). Inside the X_PCSD_AI FP, I've changed the VBA code to use the USER (replaced all SIGlobals to USER) and also changed the reference to use USER (unchecked SIGlobals). I made changes in the USER color table to be able to see the difference on FPs, but when running DV Operate, both FPs (original and X) have the same alarm colors.
Do you know if are there any other place to make changes in order the have the SIGlobals and USER running at same time?
Samuel,
Did you double-click on the alarm activex control and change the color table there as well?