Hello,
We have over 3000 Hart devices and I can not connect to any of the devices AMS Device Manager.
This is the error message I get on all HART devices in AMS:
http://i.imgur.com/Y4UbVtL.png
May I please have some help on fixing this problem. Thank you
In reply to Tinh Phan:
Tinh Phan said:There a number of situation that could result in this message. Just some thoughts of things you need to check: 1) are your DeltaV Analog channels are enabled as HART channels, downloaded, then auto sensed for HART devices 2) where are you getting the error message? AMS server plus or client? 3) have you try doing a SCAN All on the AMS Server Plus 4) what version of AMS and DeltaV are you using?I can help trouble shoot if I can get a little more info
Thank you so much for help. We are in the middle of start-up and commission as well. So I/E technician needs AMS for troubleshooting.
1. Yes
2. I see Error on client RTS1. I have not tried Pro+ or AMS Server to try and connect to device. I will try now.
3. No have not try to Scan All. Can I do this from the RTS1?
4. AMS 12.5.000.106 and DeltaV 11.3.1
Thank you so much for your help and guidance.
Thank you, I just notice in the AMS Device Manager when I connect to AMS from RTS1. http://i.imgur.com/9fuYtjT.png Do you know how to make AMS run on RTS1?
When I look at DeltaV desktop, it shows AMS is running http://i.imgur.com/aowCiLl.png Thanks