Hi,
I convert logic from 10.3 to 12.3 and also graphics.Now from faceplate Control module is not opening.
Following Error Appeared.
Error Number :53 (35)
File not found.
In reply to Youssef.El-Bahtimy:
In reply to NT4MaximusD:
In general, if you see anything starting with an "FRSZ," that is a factory-protected object that isn't accessible for view/edit, as it's locked in the VBA project. There are also many disclaimers stating that the operation of these functions and variables can change between DeltaV versions.
Assuming the VBA in your faceplate is correct. frszDynamoOpenCS utilizes the frsVariables | apps_glb | gs_control_studio_exe variable to determine the application name to launch. You can verify what this variable is defined as in Operate (Configure), and browse to the above path under the Globals folder. If InitialValue is cs, then you're using an old version of frsVariables. **DO NOT EDIT FRSVARIABLES IN-PLACE!!** This is changed between DeltaV versions, and you could wind up with much worse OI problems at your next upgrade.
I'd suggest going to C:\DeltaV\iFix\PIC and copying all of the files with extension "FXG" to your DVDATA\Graphics-iFix\PIC directory. Exclude SIGlobals.fxg and User.fxg, as these are meant for customization by integrators and end users, and there may be custom scripting / variables in these files.
Re-open Operate (Configure) and check the value of gs_control_studio_exe (CS or DVCS?). Switch to Run mode and make sure the faceplate button works.
Also, I very much agree with Adrian's comment. While DeltaV is designed to be easy to install and use, upgrading a system is a non-trivial set of tasks, and many things can go wrong. As an LBP who's done more than a few upgrades, experienced Emerson support is crucial to project success.