Anyone add an AI card to AB Flex I/O on DeviceNet?

We have quite a few Flex I/O devices on our DeviceNet segments.  We have always used discrete cards until recently.  We tried to add a T-couple/mV card (1794-IT8) recently without success. The default for this card is 11 input words and 4 output words (22 and 8 bytes).  When I change the device properties to include this card, the device quits communicating.  This is typical if you don't have the right byte sizes.  I have played around with the byte numbers w/o success.

2 Replies

  • Try A/B's RSNETWORX software using RSLYNX and their devicenet modem.  It will give the byte count.  Alternately, connect the device to DV BUT with a different devicenet ID.  Then it will show up in diagnostics with the in/out byte count.  RSNETWORX is still preferred as with it you can print the memory map.  I have done scaling with AI/AO cards.  Use the largest word size available to conserve DST's (you can decompose AI/AO/DI/DO from it and thus save DST's -- 2 for one for analog, 8 or 16 for 1 for discrete).

  • In reply to Frank Seipel:

    We are in the process of adding the 1794-IE8 Analog input card. I will report back what we did.