hi,

i have a dc function block and want to control it by a DO signal that the name is RUN STATUS. when it's 1, want to have RUNNING on PV_D and when change it to 0, PV_D equal to STOPPED. what shall i do? help me

  • You should use a DI block with the On/Off words as Running and Stopped. 
    If you have to use a DCD block for some reason configure the DCD with IN1 as your field DI. Set the DCD mask so that all inputs and outputs except IN1 are don't care. Then the DCD will show the motor as running or stopped depending on field value.

    Steve Linehan