Hi all,
Today I try to download some upgrade not related to Batch. Then after the some download on a stream, I try to ask the operator to run the stream. From BOI (Batch Operator Interface) they create new batch ID and so on. But after they done usual run then they set the mode to O-AUTO, the batch sequence was not load onto the Control Module to create the Batch Parameter and so on. Is there any tips on how to make sure it is Batch is correctly load from BOI.
Sorry I'm new in DeltaV program.
p/s: Now suddenly OK by itself, can I know what are the problem related.
When there is a problem with a recipe, it won't load in BOI. The state will say 'load_failed'. Right clicking the batch will give information on the failure. Recipe studio has a verify recipe option. This will check if all the SFC logic is valid and other things. Also when a recipe loads in BOI, the mode is o-auto by default, so I don't understand why an operator must change it. Unless ASC is used. Your question is too unclear to properly answer. More information is needed first.