I am setting up DeltaV to be used as a "wireless manager" at a customer site with DeltaV Ready Wireless Gateways (1420).
I would like to output PV/SV/TV/FV, Alarm and OINTEG/STATUS information for each wireless device and display it on an operator graphic to show a matrix overview of all devices in the plant.
Is there an easy way to be able to assign a DST (such as LT-2160) as a variable in the control module just once and then have the control module reference that "variable" for each of the output blocks? (e.g., LT-2160/COMM_ALM, LT-2160/MAINT_ALM, LT-2160/HART_PV, etc.)? Do I have to change every output block manually per each instrument to get the data?
Thanks!
Paul Acquavella
Paul,
I have done something similar for customers before but it was only be used at the graphics (SCADA values). Are you looking to just display on a graphic or actually use the value(s) in a control module?
Regards,
Matt