Hello,
I have a question please.
I have a PID setup with Track in Manual and Track Enable control options as True. TRK_VAL = 100.
When TRK_IN is equal to 1, the PID goes to MAN, and output goes to 100%.
Questions Please:
1. While TRK_IN = 1, PID goes to Man, and OUT=100%, will the Operator have the ability to adjust the output (ie., move it to 50%, etc.)? Or will the OUT remain 100% as long as TRK_IN = 1 and Operator can not adjust?
2. Will PID mode return back to AUTO after TRK_IN = 0?
Thank you
In reply to Lou Heavner:
By default the PID block will take the Actual Mode to Local Override like Lou indicates and the Target mode is unaffected. The output will be locked to the value of TRK_IN and can't be modified either by operator or the PID algorithm. This means that when the tracking conditions clear, the actual mode will go back to what the target is and allow the operator to change the output or could also mean that the output will start to control from the track value (100% in your case).
I have seen custom configurations that will drive the Target mode to Man when tracking conditions are detected but I haven't seen them return the mode back when the clear. I believe that the intention of this was to have the operator put the loop back into service by changing the target mode from Man.
Regards,
Matt
Ability for the operator to have access to the output while tracking is ON depends on option in the PID. Yes, the MODE is not impacted by the tracking action.
I don't believe that there are any options in the PID block that would allow the operator to adjust the Output when the block is tracking - the actual mode goes to Local Override (LO), which means that the block output is driven solely by the TRACK_IN value.