I would like to ask few question since I'm still new user in this DeltaV.
For now at our site some of the " Control Module " have an unexpected errors. Already ask and seek for support from Emerson at my site but still can't find the solution.
The error are :
1. When try to open up " Control Studio " this error occur, we already try many thing even no other user online to run the control module.
2. This error came up after using terminal server for several minutes.
Your co-operation are highly appreciate. Thanks.
In reply to cbpun:
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products
nikfly@gmail.com
Where is "what Youssef Suggested"?. Here is a screen shot of how the thread has updated. The response I made that Raimi refers to is not available, possibly because I responded via email. The response is in a screen shot below, then in text to ensure indexing. (just in case it somehow made it to the subscriber's distribution but not to the actual forum thread)
Raimi,
Please open database administration on the Pro plus and observe if any database connections exist from the cited workstation. If so,and you can confirm no open applications running on that workstation (control studio appears as cs.exe in task manager for instance), then disconnect the connection to the control database. If cs.exe exists when enumerating tasks from the cited user(administrator) on the cited workstation, then close or kill the task if disconnecting from dbadmin doesn't remove the task.
Youssef El-Bahtimy | Systems Integration Technologist
PROCONEX | 103 Enterprise Drive | Royersford, PA 19468 USAProconex Office: 610 495 2970 | Cell: 267 275 7513Youssef.El-Bahtimy@ProconexDirect.com
In reply to Youssef.El-Bahtimy:
In reply to Raimi: