Control Loop Tuning
Hello,
I have a puzzling question or concern. I am still a bit new to Automation, but learning.
Often operators at my plant will show me a control loop (flow, pressure, etc) and state the the valve is swinging (oscillating) all over the place. Then there is a request for me to tune the loop.
One of my biggest concern is that, "what if there is some other instrument, I/O communication, valve, positioner, etc malfunction that causing the overshoot or instability in the loop". I don't want to just start tuning a loop without proper investigation of the entire loop to make sure maybe valve is not funcitoning correctly.
Is there anything I can read related to proper diagnoistics of a valve assembly as it relates to tuning a loop?
Is there a program in DeltaV I can use to monitor the loop performance to see how the loop performs for all process conditions?
Like now, I have a loop with PV Scale of 0 - 3000 pph, loop is in manual, the PID out is 10% (and valve is showing 10% open), and the PV is 1600 pph. It doesn't make sense to me how the valve can be only 10% open while operating at 1600pph which is the mid range of the scale. maybe I am confusing my self.
Thanks for the help.
  • In reply to neilrbrown:
    Thank you neilbrown fore responding. Sorry for the delay in response.
    Your response is educational.  I have about 2-3 years experience in automation, but mostly on the instrumentaiton side. About 1 year of DeltaV experience.
    I will try what you recommended. Can I use DeltaV (maybe Process History) to trend both the commanded valve position (analog output) and the actual position (positioner feedback) parameters and make some manual output changes.
    Yes this is a flow loop.
    Thanks