Dear All,
in my project, some signals have been added that generated by analyzers. these signals are 4 wires (it means DCS cards should be Passive), but i have only some AI cards 16 CH with 2 wires Terminal Block ( Active AI Card).
is it possible to use the existing AI modules (Active AI Cards) for these kind of signals? if Yes, how can i use the 16 CH AI cards for 3 wires signals?
Thanks and Regards
Pouya
In reply to Pouya:
Dear Pouya,
That is right, it should work if you field equipment isn´t using some odd voltage in analog loop. (e.g. Siemens s7-1200 AO is 15 volts max... ).
Connect one loop and see if it works.
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products