I need to callup a function block faceplate for an AO function block. This functionality is not available (as for an AO faceplate).
Now I can create my own faceplate (I did) and my own function block faceplate (did not finish yet, but a start exists to be tested).
Now I need to call the newly created function block faceplate, which is done by calling 'frszLoad_iafb'. This function has 3 parameters:
strPic as string, strNMB as string and lngDoMonitor as Long.
For strPic only the CurrentValue of a gs-variable from frsVariables is accepted. No string "PDG_AO_fb_fp" nor User.gs_iafb_ao.CurrentValue (which is PDG_AO_fb_fp) is accepted. In the last two cases, the message "the function block faceplate PDG_AO_fb_fp could not be found". Also when another fb-faceplate (eg. pid_fb) is called, the message is the same. showing the requested filename, but no faceplate.
How can I callup a new created function block faceplate?
(DeltaV 10.3.1)
I hope this works for you:
www3.emersonprocess.com/.../drw_creating_new_faceplates_function_blocks.htm
In reply to Youssef.El-Bahtimy:
Thanks Youssef!
The two possibilities I have for calling a FB-faceplate are:
1. frszDynamoLoadIAFB "PID_TEST/AO1", Me, System.PicturePath & "\FaceplateFB\PDG_AO_fb_fp"
2. frszLoad_iafb System.PicturePath & "\FaceplateFB\PDG_AO_fb_fp", "PID_TEST/AO1", 1
It's kind of strange one has to specify in frsz routines where the fb-faceplates and dt-windows are located!
In reply to Maarten van der Waal:
I'm glad it helped.
In reply to RJA:
Private Sub Rect15_Click() frsLoadFbFaceplate System.PicturePath & "\FaceplateFB\PCSD_InSel", "010FY1404/ISEL1", frsConvertMonitorNumToDeltaVScreen(Me.pn_myMonitor.CurrentValue) End Sub This is an example that works to open the function block faceplate (PCSD_InSel) The module I opened it with was 010FY1404, which I was trying to point it to the ISEL1 block. The frsConvertMonitor.....ect puts it on the graphic you are currently on. If you want to do it on a specific monitor, just put 1-4 here.