HI guys I have a situation here,
I have 2 independent Deltav networks and both having the same PROPLUS name.
Before they were connected different External network.
Now customer wants to bring both in same network (same external LAN).
I tried to setup the same scenario in lab and found that database of 1 machine tries to access database of other.
When i remove External LAN both work properly, Even in OPCWATCHIT when i try to access database of 1 machine i get database of other machine.
Have anybody come across such situation?
In reply to AdrianOffield:
No they are not in Domain Environment , but in Workgroup (name of workgrup is also same and tried renaming workgroup but this dint solve the purpose)
In reply to Maarten van der Waal:
Are you trying to connect two DeltaV systems together to make a single system or are you trying to just connect two systems together? If it's the latter you'll need to use DeltaV Zones because you can not have two ProPlus stations on a single network without the results you are seeing. Otherwise creating a separate LAN with non 10.x.x.x addresses is the way to go.