Do you have a quad screen license? If you connect four screens the system expects to see a quad license.
In reply to GaryL:
Check the button in the graphic, maybe it is configured to: replace the primary screen
and should be: replace the current screen.
In reply to Chris:
Please check the code on the button. Some frs functions have "monitor number" in the context.
Example: syntex for function frsReplacePictureOnScreen is:
frsReplacePictureOnScreen (“NewPic”, Screen, [“TagGrp”])
where:
Screen = DV_SCREEN values as
Current Screen = 6
Default Screen = 5
Invalid Screen = 0
Max Screens = 7
Primary Screen = 1
Secondary Screen = 2
User1 Screen = 3
User2 Screen = 4
If this value is hardcoded in the functions on the button, then only the said screen will see the operation.
Regards,
Amod.