When we start a downlaod from the Pro Plus ( in the back round, runs the yellow page server), we don`t find after more hours the updated *.grf files on our OPS Stations?
The graphics download function is not instantaneous. It tries to schedule things according to network loading. If you open yellowpagesdiag on a workstation, you can watch the progress of the download.
In reply to Youssef.El-Bahtimy:
I have not checked recently but, in earlier versions of DeltaV, the time stamp on the files made a difference. On a development system, we accidentally had the time zone of one of the Op Stations set wrong and it was not being updated by yellow pages because YP saw the files on that station as newer than the ones on the ProPlus.