I have a plant problem which when switch over happens in controller level, The modules which contains DC function block gives a alarm and this alarm produce a serious problem.
DeltaV Version: 8.4.1
The observed error description: confirm time error, unresolved reference
Be part of solution, not part of problem
I have a plant problem which when switch over happens in controller level, The module with Dc block give a alarm and this alarm produce a serious problem.
In reply to AdrianOffield:
Dear AdrianOffield, Thanks for your reply, but actually the problem is in switchover-ed controller not another controller. The message parameter for this alarm was "Confirmed time". I have done a bit further search in internet and find following Issue:
Incident: 52190
>>>
Description: On a controller switchover the DC Function Block back calculates the SP value from the state of the outputs. This can present an incorrect alarm if the “Passive on Active Confirm” option is selected and the device is in the Active State when a switchover occurs.
Current Status: This Issue has been resolved.
<<<
But I couldn't find the relevant HotFix number which resolved the issue.