Hello,
When downloading the ProPlus, I get the following error:
error code 327781, RTC_NO_FB_DEFINITION_EXISTS
So, no download is proceeded.
Do you have any idea?
Thank you!
Hi,
I recently ran into the same message. It happened after I reassigned an equipment module to one controller to the other. I ran into some problems, I deleted the module from the old controller and then tried to download it to the new controller (from DeltaV Explorer). I solved it by downloading the module from Control Studio.
I would say that the cause had something to do with linked composites: some of the composites which were on the old controller were not downloaded to the new controller before downloading the equipment module, so it did not find their definitions and the download failed.
So, basically I am still not sure about the cause but the solution seems to be to download the faulty module from control studio.
Istvan
In reply to István Orbán:
after Equipment Module customization in the Library, I wanted to Download the the 4 concerned Equipment to the controller, and this Error message (error code 327781, RTC_NO_FB_DEFINITION_EXISTS) appeared. Somebody know what's the best way to solve this problem ?
Many Thanks