Profibus alarms

Hi,

In previous versions of DeltaV (we are using 11.3), when the profibus cable was disconnected(had comms loss), we got a lot of alarms in the alarm list. Now, we don't get anything. Is it a setting somewhere we are missing, or our profibus isn't set up correctly, or this is the normal behavior in version 11.3? 

Thanks,

Tibor

1 Reply

  • In contrast with FF instruments, Profibus devices do not have their own faceplates or alarms.

    The alarms which you should get should come from all the control modules which have I/O assigned to the disconnected section. These shouldb be PVBAD / MODBAD alarms.

    If you are not getting anything, check that the disconnected section is used in your control strategy and that these alarms in the control modules are enabled.