Recognition of 644h temperature transmitter

I'm a professor of Chemical Engineering at the University of Puerto at Mayaguez and I have a new Foundation Fieldbus temperature transmitter installed in one of the unit operations.  I connected the transmitter to my FF port and defined the tag in my FF card.  However, the card seems not to recognize the transmitter and when I checked the properties, it did not show any ID.  I guess this is wrong so how do I make the card to recognize the transmitter?  In the I/O list, when I check the FF card, the transmitter tag appears with a ! sign.

Any help?

--
Dr. Carlos Velazquez
Professor
Site Leader ERC on Structured Organic Particulate Systems
Director Pharmaceutical Engineering Research Laboratory

Department of Chemical Engineering
PO Box 9000
Mayaguez PR 00681

of: (787) 832-4040, ext 2576
fax: (787) 834-3655
email: carlos.velazquez9@upr.edu
            uprmpharmeng@yahoo.com

3 Replies

  • Creating a Device Placeholder

    Device support files must be installed before you can add a device to the segment or create a device placeholder. The DeltaV system includes built-in support for a number of fieldbus devices from different device manufacturers. The files necessary to support these devices are included in the DeltaV install image and are available in the DeltaV Explorer library (DeltaV System / Library / Fieldbus Devices). If a fieldbus device is not included in the DeltaV install image, you must install a set of device support files for that device. Many device files that have been tested with the DeltaV system are available from the main DeltaV website under Resources. If the device files that you require are not available on the website, contact the device manufacturer. Refer to the Device Descriptions and Methods topic for information on how to install device support files.

    About Device Placeholders
    A device placeholder is an electronic representation of a device that exists in the DeltaV database with no associated physical device. You can use a placeholder to configure block parameters offline and have your control strategy in place prior to attaching the device to the segment. When you are ready, you can attach the device to the segment and use the DeltaV system to reconcile any differences between the placeholder and the device when you commission the device.

    Note The use of placeholders is optional and depends on the size and requirements of your fieldbus application. However, it is recommended that you use placeholders for large applications. If you do not want to use placeholders, you can attach your devices directly to the segment.

    1. Click Start | DeltaV | Engineering | DeltaV Explorer to open DeltaV Explorer.
    2. Navigate to the fieldbus ports. The ports are under the H1 fieldbus card. The card is under the I/O subsystem.
    3. Right-click the port to which you want to attach the device placeholder and select New Fieldbus Device. The Fieldbus Device Properties dialog opens.
    4. Enter the appropriate information about the device in the dialog box. The DeltaV system selects an address. You can customize this field, but it is not necessary. Select the device type and revision based on the type of device you want to add. The device properties must match the properties of the device you will commission later. Remember that DeltaV Explorer has extensive online help. Click the Help button on this dialog box for help on any of the fields.

    Fieldbus devices often provide error detection for a variety of device conditions. Refer to Device Alarms Overview and Configuring Device Alarms for more information. Select the Alarms and Displays tab in the Fieldbus Device Properties dialog to enable Device Alarms to be reported by the device.

    Note The alarms and displays tab is only shown when supported by the DeltaV hardware. Device alerts are supported by Series 2 H1 cards.

    Each device can also be configured with a primary control display and faceplate. DeltaV software includes a standard device faceplate.

    1. Click OK to add the device placeholder to the segment. The device appears as a decommissioned device on the segment.
    2. When device alarms are enabled, alarms become visible in the right pane in DeltaV Explorer when you select the Fieldbus Device Alarms icon for the device. Select an alarm and right-click properties to enable or disable it or to change the alarm's priority.

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    nikfly@gmail.com

  • In reply to Niklas Flykt:

    Commissioning with the DeltaV Explorer and the Device Commissioning Wizard

    1. Attach the device to the segment.
    2. Click Start | DeltaV | Engineering | DeltaV Explorer to open the DeltaV Explorer.
    3. The device should appear under Decommissioned Fieldbus Devices. It may take a minute for the device to appear. Tip: Press the F5 key to update the list.
    4. The device must be in the Standby state before you can commission it. To determine if a device is in Standby, select Decommissioned Devices, click View | Details from the menu bar, and be sure that the words "Standby Fieldbus Device" appear under Type in the right pane.

    If the device is not in Standby, select the device in the right pane, click the right mouse button, and select Standby. It may take a minute or so for the device to transition to Standby.

    1. Now be sure that the decommissioned device's properties, Device Type, Manufacturer, and Device Revision, match the placeholder properties. To check the properties, select the item, click the right mouse button, and select Properties. If necessary, edit the placeholder properties to match the device properties. (For information about how to create a placeholder, refer to the Creating a Device Placeholder topic.)
    2. Select the device from the Decommissioned Fieldbus Devices list and drag it to the placeholder.

    The Device Commissioning Wizard - Start opens.

    1. Read the information on the Device Commissioning Wizard - Start dialog and click Next to open the Device Commissioning Wizard – Reconcile Device dialog. Use this dialog to reconcile any differences between the placeholder and the device.
    2. Click the Reconcile Device button. (If you do not click this button and click Next instead, the parameters in the device will remain as they are and will overwrite the parameters in the placeholder when you commission the device.) The Reconcile Device dialog shows two sets of fieldbus device configuration parameters: parameters in the placeholder and parameters in the device. This dialog allows you to transfer parameters from a placeholder to a device and edit parameters in the device. Click the Help button and read about reconciling device parameters. Click the Transducer block in the upper left corner of the Reconcile dialog to reconcile the transducer block parameters. Read the device documentation before reconciling transducer block parameters.
    3. Click OK when you are finished reconciling parameters and then click Finish to commission the device.

    It may take a little while to commission the device. Several factors contribute to the time it takes to commission. Among these are the number of function blocks and devices and the time it takes for devices to move through the various device states.

     

    Automatically Commissioning Fieldbus Devices

    The DeltaV system supports the automatic commissioning of Fieldbus devices when AMS Device Manager is installed. When fieldbus device auto-commissioning is enabled as a DeltaV system property on the ProfessionalPLUS workstation, it is possible to automatically commission a fieldbus device on a segment by simply attaching the device to the segment as long as the device to be commissioned matches the manufacturer, type, revision, and device tag of a configured device placeholder in the DeltaV Explorer. Refer to Creating a Device Placeholder for more information.

    Note It is important that the placeholder is created before the device is attached to the segment. The device will fail to commission if it is connected to the segment before the placeholder is created.

    To enable automatic fieldbus commissioning, select the active database in the DeltaV Explorer, select Properties from the context menu, and select the Enable Fieldbus Device Auto-commissioning option. The active database is at the top level in the DeltaV Explorer hierarchy. An icon depicting a factory is used to indicate the active database. By default the active database is DeltaV_System.

    Niklas Flykt 

    Klinkmann Oy

    Key Account Manager safety products

    nikfly@gmail.com

  • In reply to Niklas Flykt:

    Was the problem resolved? Did the device appear under "decommissioned devices"? If not I can provide a list of points to check