Hello Everyone,
We have a heavily loaded SX controller (low CPU expansion) which has some Profibus DP cards running on the maximum baud rate. Would slowing the baud rate have any impact on the CPU load? We would not be changing any module scanrates. I assume not.
Andre Dicaire
In reply to Andre Dicaire:
Not sure how much work you want to do but if you have configurations that are using CND blocks for interlocking and have "empty" Expressions (i.e. FALSE) then changing to use DCC block (v13+) and modifying NUM_USED to 0 or only the number of CNDs actually being used would lower your loading (Example below). Depending on the number of CNDs that aren't being used this has shown to be significant decrease with systems with a lot of "unused" CND blocks for interlocks/permissives.
Granted this will also affect your displays but just depends on your need to retrieve some "free time" if this amount of work would be worth it.