I have installed DV on a Proplus after settting up redundant IDDCs. I gave my domain credentials during the install when asked and the PP was joined to the domain. Good, I logged in with domain account. Good. Workstation Config finished. Now after that, next step is to log in and download the PP, Setup workstations, create config files and etc. However, my first attempt was to again login with domain administrator, but now I get a "time and date difference exists" error and it won't log me in. So, I log into the local machine with the Emerson account. That worked. However, the DeltaV services don't start. Hmm. okay. So, I see the DeltaVAdmin account listed under the login in Services. So, I don't know what the default password for DeltaVAdmin is. Couldn't find reference in a KBA. No problem, I go to my IDDC and change it in the active directory. Okay, good. So, now I log into the domain with DeltaVAdmin. Still DV services don't start. So, I try the domain admin login again. This time I don't get any time and date error. But DV services still doesn't start. So, basically I don't know what i'm doing.... LOL. I'm going to just login with DeltaVAdmin and manually start the service and go on with life.. but I have a number of other workstations to setup and want this to go smoother.
Thanks
In reply to Nick Mason:
In reply to TreyB:
Check in services that Remote Procedure Call (RPC) is running and its Startup Type is Automatic as shown below. You may need to correct the Startup Type if it is not set to Automatic and may need to manually start the service if it is not running.
The utility is in the \DeltaV\Bin directory to update the password for the DeltaVAdmin account - ServPwd.exe. You need to do this on all workstations.
In reply to David-m.walker: