Hi,
Could anyone help explain our situation please?
DV-3 is an MX controller, DV-1 and 2 are MD plus controllers, we are running version 13.3. all controllers have power and backup supplies and we run with a UPS.
Our problems started, as you can see on first pic controller_fail_1, with losing coms to our 3 controllers, first DV-3, then DV-1, then DV-2, what followed was lots of switching for all our devices back and forth between our two switches, but only DV-1 and 2 seem to be mentioned, DV-3 isn't mentioned again until much later when it goes through a cold restart, as seen in pic controller_fail_2.
Upon investigation one of the power supplies for DV-3 had tripped, but the primary is still operational, for DV-3 to go through a cold restart doesn't that mean that the controller lost power?