I am having trouble finding the source of a MODBAD Alarm.
The operators tell me that a certain motor, when it is started, usually give a MODBAD alarm. I haven't been there to witness it, but the Event Chronicler shows a MODBAD event, and gives the detail: Module Error 264.
My suspicion is that the motor is drawing high starting current, and the CT is delivering over the 20mA to the AI CHARM.
If that is the case, what can I do in this situation? The supervisor is concerned the operators will become numb to this alarm, perhaps leading to apathy for other alarms.
I know motors can draw 5 to 13 times their FLA on startup. Is there a way to mask an input transient in a CHARM?
Thanks in advance.....
Ralph Kitts
Can you please check how MODBAD_ALM was configured? This is how it looks like for one of the templates.
If you have the same configuration as above, kindly share contents of the CND block. If it is tied to BAD_ACTIVE, can you please share values of MERROR when the issue occurs?
Below is an example of a module with bad input.
In reply to Matt Stoner:
In reply to Ralph Kitts:
Andre Dicaire