We are running Emerson RM-100 switches and would like to set up one of the free interfaces to mirror the uplink.
What I have found so far is that this feature can be set up using a telnet session, however, I am not exactly clear on the proper command structure. For my particular use case, I would like to mirror 1.1 to 3.8
The switch gives me this breadcrumb but I would feel better if someone had an example for me to reference.
'monitor session <session-id>
{mode | {destination|source} interface <slot/port> }'.
Does anyone have additional information about this command?
In reply to Alexandre Peixoto:
Ahh, i was missing the DeltaV part and only running the monitor command.
It was straightforward after that. Attached is an example for future reference.
(Emerson RM100) >deltav monitor Do you want to delete the current Port Mirroring Configuration? (y/n): y Mirroring Session cleared. Enter Probe Port e.g 1/1: 3/8 Configured probe port is 3/8 Enter List of Mirroring Source Ports to be added: 1/1 Adding Mirroring Source Ports completed. Current Mirroring Source Ports are: 1/1 Do you want to activate the current Port Monitor Session? (y/n): y Mirroring Session is enabled. Do you want to save the current configuration? (y/n): y Saving Configuration (Emerson RM100) >monitor