Got CMF050 Flowmeter for Refrigerant flow measurement.
Model: CMF050M320N0A2EZZZ
Transmitter: 2400SIA11B2EZZZ which gives 4-20mA output.
Measuring range of the sensor – 0-57.6 kg/min.
Given transmitter 24VDC power supply to L1 & L2 and have taken current output from CHA + and – of the transmitter
For initial commissioning, We used a water pump which is giving a constant flow of 13-14 kg/min approx.
At Flow meter display flowrate is shown as 13.2kg/min, whereas the current output is 5.44mA, which corresponds to 5.13Kg/min.
Hence there is difference between the display and current output by the transmitter.
Also we observed that the density of fluid (Water) changes with the change in flowrate.
Answers welcome to solve this issue.
Stefan Müllner Senior Plant Engineer - Automation & Systems
KremsChem Austria GmbH
In reply to Stefan Muellner:
In reply to Prithvisaran:
In reply to Tonya Wyatt:
Prithvisaran - Here is a link to the configuration manual. https://www.emerson.com/documents/automation/manual-2400s-configuration-use-manual-micro-motion-en-62556.pdf
Thanks, Tonya
Hey Tonya ,
It is working now issue is cleared after mA configuration change in the transmitter
Tonya Wyatt Stefan Muellner Thanks guys for your support.