At times we need to shut a pump down and work on it and not have anything else that is interlocked with the pump shutdown. Normally we bypass the conditions in other modules that look at the pump's status. Every once in a while we get into a situation where that is not the best solution. In those conditions we have tried enabling simulate. However once we turn on simulate the digital out that writes to the field IO remains energized. It remains energized even if we change the SP of the DC block to STOP.
The DC block SP is stopped but the field IO is energized. The result is the motor starts whenever power is reapplied to the pump motor. A 500 HP motor starting without expecting it is not a good thing.
Is there some way to simulate the status of of DC block to running but also be able to turn the field IO off?
We are version 11.3 1