Looking to see if anyone has accomplished this or can help me create a way to automatically perform this procedure
Here's our set up: two 50 Inch screens that are used as trend stations
Procedure:
1. Operations opens up PHV
2. Browses for the most used charts (6 of them)
3. Stretches and positions each Chart
4. Clicks File/ New instance to open up another PHV application for the second screen
5. Browses for the most used charts (6 of them)
6. Stretches and positions each Chart
Problems:
1. Takes ops about 15 minutes to get the trends just right, which means they are distracted for about 15 minutes
2. Makes Ops grumpy when we need to do windows updates/ hotfixes and must close down their station
I'm sure there has to be a way VIA schedule or a button using VBA to automate this so that the Computer Opens instances/ fits the charts. Not quite sure the best way to do it.
Thanks Emerson Community!
Shamusk
Andre Dicaire
In reply to Andre Dicaire:
Here is what our graphic with embedded trend looks like so far. As far as I can see there is no way to get rid of the Y scale. Is that correct?
In reply to Shamusk:
I pulled up an Embedded Trend to configure tags and I think the New Axis check boxes can be deselected to hide the Y axis EU values.
The Y scales can be hidden on the pen properties dialog. If you click both , the scale is on both sides.