Hi All,
We are trying to interface Micro 870 PLC with delta V DCS EIOC(firmware rev: 13.3.0.5788) controller via ethernet. There are 4 options in delta V EIOC Ethernet comms. We tried ‘UCMM for logix tags’ Option and ‘Explicit messaging with PCCC’ Option, but with no avail. I presume 'UCMM for logix tags'option is suitable for control logix/compactlogix PLCs and 'Explicit with PCCC' option is suitable for Micrologix PLCs. Delta V EIOC is able to see the Micro 870 PLC, but not able to communicate.
The only option we are left with are ‘Class1 Implicit messaging’ and ‘class 3 explicit messaging’.
I am not sure of the communication settings to be configured for both types. It would be helpful if someone can shed light on the following parameters
For class 1 implicit messaging:
Input assembly Instance ,Output assembly Instance, Configuration Assembly Instance
For class 3 explicit messaging:
Class ID, Instance ID, attribute ID
In terms of communication, we need 12 INTs to be sent across to the Micro 870 PLC and 4 INTs to be received from Micro 870 PLC. Every tag in Micro 870 has been set as global variables, so CIP enabled device can communicate to the tags we need.