Hello,
I am working on a project where I need to be able to do compensation according to the API tables. I don't see any function blocks in DeltaV that provide this. Is there a way to interface with these tables and get the appropriate correction factors?
Thanks,
Dave
Dave,
I was looking for the same thing awhile back. I ended up using the following document:
The document list out coefficients based upon product grouping.
Prior to the table it shows the different formulas to use and examples to go by. This is what I ended up doing for tank volume correction based upon temperature.
Chris
In reply to Chris Kominar: