We are at Version 11.3.1. We just uploaded our controllers in preparation for a possible hurricane strike. After we did the uploads, we decided we also should have also uploaded the setpoints of the PID's. Is there a way to force an upload of specific parameters such as setpoints only?
In reply to Jason.Brumfield:
This functionality was actually added in v14 under parameter security with the interface shown below
Modifying the parameter (or adding) will have an "Allow Upload" check box to determine if that parameter name should be able to be uploaded along with the traditional setting of the associated Lock.
Andre Dicaire