Upload from controller

Dear friends,

assume my workstations have in problem and the database is totally deleted. how can i access to the logic that was downloaded on controller? does it need to special software? uploaded file (software output) has the totally logic that downloaded on controller?

2 Replies

  • Please explain your hypothetical situation in more detail. If the offline database on the ProPlus is deleted, you can simply reload the database from a backup file that we call the FHX. The FHX file is a flat text file export of the entire database. Database Administrator Tool even lets you schedule a daily backup of the FHX.
  • It is not possible to upload the configuration from the controller, just the current value of parameters. Backups and exports of the database are an absolute necessity to prevent losing your configuration. Do it now and implement automation/policy for the long term, before it is too late.