dear friends, is it possible to connect m-series to CHARM?

shall we consider s-series as CHARM? is it true?

best regards

  • As per my knowing, M Series does not support CHARMS, only S-seies can support charms, but in DeltaV 12.3 version or above, it can support Mix system of M-series and S-series
  • Version 14 allows M-series controllers to work with CHARMS.
  • In reply to Ottozeng:

    Thank you my friend...
    as per your quote, the traditional M-series of I/O will work with CHARM. good!
  • In reply to JoshC:

    thanks for replying
    what about for previous version?
  • In reply to semova2:

    CHARMS were released on v11 and were supported on SX, and SDPlus, and later also SQ. S-series and M- series are supported together on every release since v11. Prior releases support Mseries only.

    SIS CHARMS were released in v12 with SZ controller. M series and S series controllers can share peer to peer data.

    V14 introduces PK controllers and along with S series and M series all controllers can have CHARMS.