I have a PID flow loop in DeltaV (12.3.1) that is showing 4/20mA AO1 output, but the database (offline) indicates 0-100%.
Downloading the CM does not change the runtime value to match the database value.
Backstory -
I was downloading a PV range change, and the upload report flagged that the AO1 XD_Scale had been previously changed in runtime to 4/20mA.
I chose poorly and uploaded the change. We have since changed it back in the Database and re- downloaded -
But it remains unchanged in runtime:
Short of deleting the CM and restoring it from a previous version, I don't know what to do.
In reply to girishbm1:
Thanks again Girish -
I'm looking at a Westlock ICOT, and I'm not seeing the settings you have. Have auto sensed again, this is what I see:
In reply to SimHogan:
Hello SimHogan,
I am not 100% sure about the Westlock ICOT as the setting that I showed are for DVC. However I am thinking that the below highlighted setting could be the one that has issue. If you can try then I would suggest putting the device in 'Out of Service' from AMS; this could enable the 4-20ma OR 0-100% option slection in the configuration page.
Here's the update (short term fix)
I switched the CHARM to non-HART, standard 4/20mA, downloaded the CHARM, then downloaded the CM. Now AO1/OUT looks normal.
Thank you very much for pointing me in the right direction.
Sim